Sensor Module and Rack AIC ratings
Module/Rack AIC Ratings
A.I.C. is an acronym for "Ampere Interrupting Current". It is measured in Amps (A), or thousands of amps (kA). The AIC rating is the maximum current that can flow through a piece of equipment without permanent damage. If a direct short is occurs, this is important in determining whether the circuit breaker trips fast enough to prevent damage or injury.
ETC supplies these values for our power control systems; they should be used by a professional electrical engineer to design a safe and standards compliant system.
Sensor SR/SRN Series Racks
Sensor racks are a modular system. The module in the rack with the lowest AIC rating determines the AIC rating for the entire dimming rack.
For Unison DR Series Racks
The racks have the following AIC ratings:
DR6 | Maximum of 10,000 AIC |
DR6 at 277V | Maximum of 14,000AIC |
DR12 | Maximum of 22,600 AIC |
DR12 with Aux Rack | Maximum of 66,800 AIC |
You apply the DR rack rating first and then, the dimmer module in the rack with the lowest AIC rating determines the AIC rating for the entire dimming rack. (A D20 with an AIC of 100,000 in a DR6 would give you a total AIC for the installation of 10,000)
AIC ratings for Dimmer Modules
Model # | Description | Risetime | Voltage | AIC | Compliance | Notes |
D15 | Dual 1.8kw dimmer | 350uS | 120v | 100,000 | UL, cUL | |
D15E | Dual 1.8kw dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D15AF | Dual 1.8kw dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D15AFN | Dual 1.8kw NC dimmer | 500uS | 120v | 100,000 | UL, cUL | |
GFCI modules were discontinued in 2014 | ||||||
D15F | Single 1.8kw (3 wire Fluorescent) Dimmer | N/A | 120v | 100,000 | UL, cUL | |
CC15 | Dual 15A Constant Current Circuit Breaker | N/A | 120v | 100,000 | UL, cUL | |
BC15 modules are discontinued | ||||||
R15AF | Dual 1.8kw relay | N/A | 120v | 10,000 | UL, cUL | |
D20 | Dual 2.4kw dimmer | 350uS | 120v | 100,000 | UL, cUL | |
D20E | Dual 2.4kw dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D20AF | Dual 2.4kw dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D20AFN | Dual 2.4kw NC dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D20AFG | Dual 2.4kw GFI dimmer | 500uS | 120v | 100,000 | UL, cUL, UL943 | |
D20HR | Single 2.4kw dimmer | 800uS | 120v | 100,000 | UL, cUL | |
D20F | Single 2.4kw (3 wire Fluorescent) Dimmer | N/A | 120v | 100,000 | UL, cUL | |
CC20 | Dual 20A Constant Current Circuit Breaker | N/A | 120v | 100,000 | UL, cUL | |
BC20 modules are discontinued | ||||||
R20AF | Dual 2.4kw relay | N/A | 120v | 100,000 | UL, cUL | |
D50AF | Single 5kw dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D50AFN | Single 5kw NC dimmer | 500uS | 120v | 100,000 | UL, cUL | |
D50HR | Single 5kw dimmer | 800uS | 120v | 100,000 | UL, cUL | |
CC50 | Single 50A Constant Current Circuit Breaker | N/A | 120v | 10,000 | UL, cUL | |
D100AF | Double 12kw dimmer | 500uS | 120v | 100,000 | UL, cUL | |
ELV10 | Double 10A reverse-phase dimmer | N/A | 120v | 100,000 | UL, cUL | |
TR20AF | Double 20A configurable relay or dimmer | 500uS | 120v | 100,000 | UL, cUL | |
TR20SAF | Double 20A configurable relay or dimmer | 350uS | 120v | 100,000 | UL, cUL |