Inrush Current and ETC LED Fixtures
Inrush current refers to the maximum amount of current drawn immediately upon power up of an electrical device. This can vary depending upon the type of load on the circuit. In an incandescent scenario, inrush is high until the filament warms up and resistance increases.
The information below is to help you understand how inrush current works with our LED fixtures.  For in-depth information on how to applies to the number of LEDs you can have on a circuit and how to determine that number, please read this white paper: How Many Fixtures on that Breaker.pdf
In the case of a switching power supply like those used in many electronics including ETC LED fixtures the inrush current is much higher than the nominal operating voltage.  In some cases the current can be as much as 75 times higher for a short period of time, usually worst at the first half- cycle.
This can create an issue with circuit breaker protection for a line of fixtures all coming from the same non-dim source.  The amount of fixtures that you can use at nominal voltage that will cause your circuit protection to engage is much higher than the amount of fixtures you can use upon inrush.  To compound this, most circuit breakers have different inrush trip curves.   To find the trip curve of a particular breaker, it is best to find the datasheet of the breaker in question.  This makes it impossible for ETC to calculate across the board how many fixtures can be on a circuit as it can vary widely and is reliant upon the breaker installed in the system.
To avoid inrush problems, a good solution is to develop a startup sequence.  This means that not every fixture would be started at the same time.  This is common practice among high end audio gear for the same reason.  This allows a device to power up past the inrush point before another fixture hits its inrush point.
Below is a graphic with a scope shot of a fixture upon startup.  The green line is the current the fixture is drawing.  This is a good visual illustration of what is happening when a fixture is powered on and then how it normalizes.
ColorSource Cyc Inrush
120V- 39A (First half-cycle)
240V- 74A (First half-cycle)
  • 10 Fixtures/ R20 circuit (link up to 9 via power thru connector)
Nominal Power Consumption at Full Intensity
Voltage (V) Current (A) Watts (W)
120 1.11 133
240 0.59 116
ColorSource Fresnel V Inrush
120V- 36A (First half-cycle)
240V- 57A (First half-cycle)
  • 9 Fixtures/ R20 circuit (link up to 8 via power thru connector)
120 1.28 148.4
240 0.70 147
ColorSource Linear Inrush
120V- 35A (Linear 1) / 35.6A (Linear 2) / 67.5A (Linear 4) (First half-cycle)
240 V- 49A (Linear 1) / 85.6A (Linear 2) / 153A (Linear 4) (First half-cycle)
  • 10 cells/ R20 circuit (link up to 9 cells via power thru connector)
Model Voltage (V) Current (A) Watts (W)
Linear 1 120 0.95 115
Linear 2 120 1.82 218
Linear 4 120 3.68 438
Linear 1 DB 120 0.92 110
Linear 2 DB 120 1.82 218
Linear 4 DB 120 3.70 440
Linear 1 240 0.48 112
Linear 2 240 0.91 213
Linear 4 240 1.82 426
Linear 1 DB 240 0.46 108
Linear 2 DB 240 0.91 214
Linear 4 DB 240 1.83 428
ColorSource PAR Inrush
120V- 35A (First half-cycle)
240V- 49A (First half-cycle)
120 0.75 90
240 0.4  89
ColorSource Spot Inrush
120V- 28A (First half-cycle)
240 V- 46A (First half-cycle)
100 1.69 168
120 1.39 166
240 0.72 166
ColorSource Spot Jr. Inrush
240 V- 45A (First half-cycle)
  • 7 Fixtures/ R20 circuit
120 1.40 166
240 0.73 162
ColorSource Spot V Inrush
120V- 55A (First half-cycle)
240 V- 59A (First half-cycle)
  • 8 Fixtures/ R20 circuit
100 2.00 199
120 1.65 197
240 0.90 194
D22 Inrush
120V- 17A (First half-cycle)
240V- 25A (First half-cycle)
  • 20 Fixtures/ R20 circuit
120  0.47 56.5
240  0.25  60
D40/ D40XT Inrush
120V- 15A (First half-cycle)
240V- 40A (First half-cycle)
120  1  110
240 0.5 120
D40XTI Inrush
120  1  110
240 0.5 120
D60 Inrush
120/240 13.5/0.68 161
240  0.68  163.2
D60 XTI Inrush
120V- 46A (First half-cycle)
240V- 77A (First half-cycle)
120 1.03 123.6
240  0.54  129.6
Desire Fresnel Inrush
230V- 46A (First half-cycle)
120 1.2 138
230  0.6 132
Source 4WRD II Inrush
120V- 30A (First half-cycle)
240V- 12A (First half-cycle)
  • 120V: 14 Fixtures/ R20 circuit
  • 240V: 6 Fixtures/ ER15AFR circuit
  • line dimming: ETC recommends no more than 1 Source 4WRD fixture per circuit for line dfimming to maximize dimming performance.
120 1.26 150
240 0.75 175
Source 4WRD Color Inrush
120V- 32A (First half-cycle)
240V- 60A (First half-cycle)
  • 120V: 10 Fixtures/ R20 circuit
  • 240V: 10 Fixtures/ ER15AFR circuit
120 1.25 146
240 0.67 143
Source 4WRD Color II Inrush
120 1.25 146
240 0.67 143
Source Four LED Inrush
120V- 11A (First half-cycle)
240V- 15A (First half-cycle)
Lustr+ 120 1.11 129.9
Daylight 120 1.39 163.63
Tungsten 120 1.35 157.4
Studio HD 120 1.07 127.1
Lustr+  240  0.56  135.36
Daylight  240  0.72  172.32
Tungsten  240  0.70  166.8
Studio HD  240  0.56  135.36
Source Four LED Series 2 Inrush
120V- 50A (First half-cycle)
240V- 107A (First half-cycle)
  • 9 Lustr Fixtures/ R20 circuit
  • 7 Daylight HD or Tungsten HD Fixtures/ R20 circuit
120 1.45 174
240  0.81  195.12
Source Four Mini LED Inrush
120V- 3A (First half-cycle)
240V- 4A (First half-cycle)
120/240 ? 14
Source Four LED Series 3 Inrush
120V- 40A (First half-cycle)
230V- 80A (First half-cycle)
  • 5 Fixtures/ R20 circuit
Lustr X8 120 2.6 307
Daylight HDR 120 2.85 340
Lustr X8 230 1.35 305
Daylight HDR 230 1.5 330